Hello all,

Please note residential refrigerator is the issue here and the load is draws alone.

Tried to plug in coach to shore power at the house, only have normal 15A outlets. I turned off all the breakers except the fridge, and kept blowing the GFI in the garage (where power is located). I ran out the 50A cord, and adaptered it down to 15A receptacle male fitting which I plugged into a 25' extension cord, as the coach is parked on one side of the lot and the closest power is on the other side of the house. I used a 25' 14/2 extension cord. I think it should have handled the load, but it did not. I have a 20A 50' 10/2 conductor extension cord I purchased for my boat, and will try it next time. Is something running which does not switch off when throwing the breakers, as I specifically turned off the inverter, and made sure the charger was not running.

I have done (as many know by my posts) the electrical transfer-surge guard switch conductor tightening job, redone the generator connections as well and have checked all the grounds as I can find them.

Any thoughts on if the coach as a matter of routine draws more than 15A, when everything is just turned off? I went into the tank bay, unplugged the refer, and ran an extension cord up to that plug and it’s now running to get cold. Nothing else is powered on; the inverter is still off, as well as the charger.
It worked the first time we brought it home, and it worked in Montana when we visited a relative and plugged into her garage power. Now it won’t run on 15A supply.

I know the grounds are good, because I have double checked them all. In Montana, we came off the 50A cord with a 25’ 30A RV extension cable, and then plugged into the house. At home I used the larger extension cord the first time, and it worked then, which may be the answer. The GFI could also be getting weak, and I am aware that once they get week, it’s easier to trip them off.


Monty & Janet
2007 Alpine APEX 40 MDTS



 
Posts: 258 | Location: Vancouver, WA | Registered: May 05, 2008Reply With QuoteEdit or Delete MessageReport This Post

Posted Hide Post
I pretty confident in saying your inverter is still using power (mine is on all the time). 15 amps wouldn't work for me. I wired a 30 amp receptical to a 20 amp breaker and now I can run fridge and 1 a/c. The breaker limits the load

Jim and Kathy
06 Apex
 
Posts: 57 | Registered: July 12, 2007Reply With QuoteEdit or Delete MessageReport This Post
"Lead Moderator"

Picture of Route 66
Posted Hide Post
It may be the inverter if you have one.

Some inverters will charge the batteries even when turned off, and they can draw quite a bit on bulk charge.

See if the inverter can be set for 15 amp service.


__________________________
Adios, Dirk

'07 Dutch Star 4029, '08 Yukon XL
Escapees 64797, NKK 17897-L, FMCA 382762, Telephone Pioneers, ATA
Navigation by Ouija Board

My Current Location My DSDP
 
Posts: 4077 | Location: Originally Newark, DE; Now The Good ol' U.S. of A. | Registered: May 24, 2000Reply With QuoteEdit or Delete MessageReport This Post

Posted Hide Post
That is what is going on with mine, always had dead batteries. You can set the amperage thru the silverleaf

Jim and Kathy
06 Apex
 
Posts: 57 | Registered: July 12, 2007Reply With QuoteEdit or Delete MessageReport This Post
"Alpine Coach Forum Member"

Posted Hide Post
Monty, if the above idea fails, you can disconnect the fridge in the basement and connect your extension cord directly.


Basil & Sue Shannon
Traveling Circus
Small show, just two clowns having fun.
Alpine APEX 40' 2006
 
Posts: 212 | Location: Full time. Home base:Corpus Christi, TX (Padre Island) | Registered: January 08, 2004Reply With QuoteEdit or Delete MessageReport This Post

Picture of Wil Rathke
Posted Hide Post
My inverter/charger control panel has the ability to disable the inverter and also the charger separately. Yours probably does also. Be sure that the charger is disabled. If the batteries are even slightly discharged, the charger will try to charge them at 100 A DC which would be near 15 amps AC. If it still trips your house CB the coach is presenting another load which is not obvious. Try running the generator with the charger on and building up an initial charge on the batteries.


2005 38FDTS
2001 Honda CR-V
 
Posts: 96 | Registered: July 17, 2003Reply With QuoteEdit or Delete MessageReport This Post
"Alpine Coach Forum Member"

Posted Hide Post
We had the same problem on our 40fdqs. Did not have the problem, then had the problem.

It was cause by the switch being set to electrical on the water heater. When I set it to propane, the problem went away.


Dennis And Sally
2005 40FDQS
 
Posts: 27 | Location: West Covina, Ca 91791 | Registered: January 05, 2006Reply With QuoteEdit or Delete MessageReport This Post
"Alpine Coach Forum Member"

Posted Hide Post
I had a similar problem a while back. It turned out that there was a lot of draw from other appliances, etc. on the garage circuit. It wasn't the coach at all.


Terry McGuire
09 Alpine Limited SE 36FDTS
06 Wrangler Toad
 
Posts: 44 | Location: Selah, WA | Registered: September 11, 2005Reply With QuoteEdit or Delete MessageReport This Post

Posted Hide Post
Cannot disable the inverter on the Apex. Thats why my batteries were dead, I could disable the charger however. I don't want to go into the basement and turn the inverter on and off all the time and even then I think it still draws power (Apex only)

Jim and Kathy
06 Apex
 
Posts: 57 | Registered: July 12, 2007Reply With QuoteEdit or Delete MessageReport This Post
"Alpine Coach Forum Member"

Posted Hide Post
Monty,

See if you have a receptacle with out GFI protection and let us know if it will work when plugged into that receptacle.


Dale Gerstel
Las Vegas, NV
2007 Alpine Limited SE 40FDTS
2007 Honda Odyssey
ACA & SoCal
 
Posts: 415 | Location: Las Vegas, NV | Registered: December 02, 2001Reply With QuoteEdit or Delete MessageReport This Post